When I had this problem I realised that my boiler thermostat was set to a lower temperature than the hot water cylinder thermostat. That meant that the boiler could never satisfy the demand of the cylinder so the motorised valve to the tank coil stayed open and the pump kept running.
Once I set my tank thermostat to around 60-65 degrees and the boiler thermostat to around 80-85 degrees it cured the problem.
@
TAYLOROY @
meldrewreborn
I can confirm this was exactly the case - I set the boiler temperature up a tad and dropped the tank thermostat to 55⁰C. The system reached this after about ½ hour, with the pump and boiler turning off at this temperature.
So I upped the tank thermostat back up to 60⁰C and it ran for another ¼ hour before turning off. (This in fact makes for a perfect comparison since the electric immersion must have run for about 40 minutes to reach the tank temperature)
So this time the gas used was 0.406m³ x 11.2 = 4.55kWh @ 7.2p: Cost=32.7p
This compared to the electric immersion of 2.33kWh @ 9.5p: Cost 22.13p, so still about ⅔ cheaper using electricity than gas! (...on Next Drive ToU tariff)
This also clearly highlights the inefficiency of the gas boiler's indirect heating of the hot water tank via the heat exchanger, since "Ye canne change the laws of physics" which state that
1 litre of water takes 1 kilocalorie (4,184 Joules ) to raise the temperature by 1⁰C
So nearly half of the energy used ie. (4.55 - 2.33)=2.22kWh ==7,992 kilojoules of energy is being wasted by the indirect heating😯
This test also has identified an issue I hadn't been aware of by not having the boiler feed water temperature high enough the water didn't reach the tank thermostat temperature so the boiler/pump just kept running, which could potentially increase cost significantly!