Great idea, please keep us updated, I’m switching to ev tariff soon and would love to see the price comparison between gas and electricity for heating hot 2 water at the cheaper rate.
@
TAYLOROY @
meldrewreborn
I ran the gas h/w only test for 1½hrs taking before and after meter readings which showed 0.542m³ usage - doing the maths 0.542 x 38.9 (calorific value) x 1.02264 / 3.6 = 5.989kWh
So based on my kWh usage of 5.989 @ 7.4p this cost 44.32p
Running my 3kW immersion until it reached the thermostat temperature took 2.33kWh
So on the Next Drive tariff of 9.5p this cost 22.13p, which is
half the cost of heating by gas.
However on a standard tariff rate of say 28p this would have cost 65.24p which is about 50% more than using gas.
It appears that (although being more expensive on the standard rate) heating by electricity is clearly nearly three times more efficient energy wise than heating by gas!
Interesting - I started the hot water test @ around 6 a.m (c/h was set to off) expecting to see the system/pump stop when the tank water reached 60⁰C
The light on the pump never went off, so the pump appeared to be on the whole time, so I terminated the test @ 7:30
I've got an old spring-mounted c/h thermometer on the boiler feed pipe which indicated ~145⁰F = 63⁰C (not sure how accurate this is)
Although the boiler must have cycled off, with the pump running for the whole period the boiler feed temperature was showing ~130⁰F=54⁰C. Since the pump was still circulating the feed-water, this must indicate the feed temperature is now being maintained by the h/w in the tank.
Worryingly, this situation would gradually cause the h/w tank temperature to drop as the tank heat-exchanger would now be losing heat to the circulating feed rather than gaining it from the boiler.
I'm sure the wiring of the controller should cause the h/w valve to close when the tank thermostat reaches temperature, and if the c/h isn't active also turns the boiler off, so would also expect the pump to stop in this situation