The boiler has a built in bypass. We keep one small radiator open "just in case" but it cant call for heat. The house is 10 years old and very warm and well insulated. We barely need to heat it even in cold weather.
@MattB
your best course of action would be to get someone competent in fault finding with a voltage tester / multimeter to get to the bottom of it for you.If its electrical then it needs the correct safety checks Carrying out on this before working on it.
Agree and thanks for your expert advice. I find it interesting in that it was not until I could monitor with a smart meter that I realised there was a problem.
Just to explain in plain English, when a thermostat calls for heat a live feed goes to the motorised valve, the synchron motor opens the valve and then trips a micro switch sending a different live feed to the pump and boiler. When the demand for heat ceases power to the synchron motor ceases and the valve closes under a spring return. The micro switch will be released and the feed to pump and boiler will cease too.
but if the micro switch contacts have fused shut due to sparking over time then the boiler will still be powered together with the pump. With all 3 valves shut the boiler will fire, get to temperature and shut down, water will circulate though the by pass units, and gradually cool the return flow back to the boiler, where eventually the boiler will fire again and the cycle will then happen again and again.
this would explain the constant gas use from midnight onwards, but not the peak at 03:00.
Posted just for the lay forum members to aid understanding.
Current Eon Next customer, ex EDF, Zog and Symbio. Don't think dual fuel saves money and don't like smart meters. Chronologically Gifted. If I offend let me know by private message, but I’ll continue to express my opinions nonetheless.
@MattB
Try putting the heating side on 'timed' and switch off a 'window' between midnight and 7am. See what happens then
Sorry...it's clearly something your Tado system is not doing properly, or you do have some electrical issues somewhere. If you manually turn the boiler off....no gas consumption.
Previously when I turned all the Tado stats to 'off' the same thing happened, so I do not believe it is the tado system that is faulty. You could argue they are calling for heat when not registering that they are, but I do not believe that to be the case.
Just to explain in plain English, when a thermostat calls for heat a live feed goes to the motorised valve, the synchron motor opens the valve and then trips a micro switch sending a different live feed to the pump and boiler. When the demand for heat ceases power to the synchron motor ceases and the valve closes under a spring return. The micro switch will be released and the feed to pump and boiler will cease too.
but if the micro switch contacts have fused shut due to sparking over time then the boiler will still be powered together with the pump. With all 3 valves shut the boiler will fire, get to temperature and shut down, water will circulate though the by pass units, and gradually cool the return flow back to the boiler, where eventually the boiler will fire again and the cycle will then happen again and again.
this would explain the constant gas use from midnight onwards, but not the peak at 03:00.
Posted just for the lay forum members to aid understanding.
the pipes from the boiler before they get to the motorised vales. If towel rails and bypass are plumbed into these they will be hot if any of the 3 motorised valves are open, or indeed if one of the valve micro switches is continuously live.
The graph I posted was intended to demonstrate the gap during the day when I switched the boiler off. Last night was very cold and in fact the tado kicked in on two rooms around 3 am because it got below the 17 degree limit so that explains the peak. But all the hours before that were again not called for by the stats.
As with every diverse community, there is always a mixture of opinions, knowledge as well as understanding - that’s what makes it such a great place to be! To make sure everyone gets the most out of our Community and feels good doing it, we’ve created some values below on how to be an awesome, positive member. So, take a read and then go for it!
We love having you all here in the Community and really hope you find some great advice and help from our other amazing members. As a community team, our main role here is keeping things ticking over, everyone safe and getting involved in some great conversations! We know many of you will have specific queries about your accounts and we want to keep your personal details safe so please don't post them here.
• Saying thanks goes a long way
• The community is a public website, so be careful
• Be kind, respectful and supportive
• It's a family-friendly community
• If you’re in a specific section or discussion, try to stay on topic
• One post is normally enough
• Be cool, don’t spam
We want to ensure that the community is safe and fair for everyone…
We all work hard to ensure everyone feels respected and supported while using the community, and keep that positive energy flowing. If a member or group is disrupting your experience without a genuine reason, you can report this to the community team quickly and easily by clicking the 3 dots on the post. Don’t worry about a thing, we’ll take it from there. If you get a message from the team about your behaviour, please try to work with us, as all we want to do is make this a positive place for everyone. In order to this, we have to uphold these Community Values and the Community Team has the final say.
The full Community Values can be viewed here
If you agree, please click the 'I agree' checkbox and press the 'Complete Registration' button below. If you would like to cancel the registration, click here to return to the Community homepage.
Although the administrators and moderators of E.ON Next Community will attempt to keep all objectionable messages off this site, it is impossible for us to review all messages. All messages express the views of the author, and neither the owners of E.ON Next Community, nor vBulletin Solutions Inc. (developers of vBulletin) will be held responsible for the content of any message.
By agreeing to these rules, you warrant that you will not post any messages that are obscene, vulgar,sexually-oriented, hateful, threatening, or otherwise violative of any laws.
The owners of E.ON Next Community reserve the right to remove, edit, move or close any content item for any reason.