I didn’t have a close handle on time periods (months) for previous bills and there were lots of estimated readings which were subsequently adjusted approximately quarterly so it will be difficult to tease that out with such a short current time period.
if there was a faulty zone valve then the boiler and pump would run? The sole radiator not on a smart valve doesn’t seem to warm up.
I am wondering what controls the four water heated towel rails.
I didn’t have a close handle on time periods (months) for previous bills and there were lots of estimated readings which were subsequently adjusted approximately quarterly so it will be difficult to tease that out with such a short current time period.
if there was a faulty zone valve then the boiler and pump would run? The sole radiator not on a smart valve doesn’t seem to warm up.
I am wondering what controls the four water heated towel rails.
You are correct if a faulty valve micro switch was allowing power through with the timer off, and not energising the valve motor then the boiler and pump would operate . Is your property zoned just using the TRV’s or do you have separate room stats/ programmers for each floor?
@Plantagenet
ground floor wet UFH in separate zone. First and second floors all in one zone with one wired stat.
There are 3 zone valves in the system next to the hot water cylinder.
One motorised valve will be for the cylinder coil controlled by cyl stat, one valve for first and second floors and the other for underfloor htg. It’s possible any one of these could be faulty if it’s the one for the underfloor heating you wouldn’t really feel any real heat unlike radiators. If you do as others have suggested and turn the boiler off at the fused spur it could indicate if it is an electrical problem causing your boiler to fire when there is no demand from any of the controls on the system.
[QUOTE=MattB;25346]@Plantagenet
ground floor wet UFH in separate zone. First and second floors all in one zone with one wired stat.
There are 3 zone valves in the system next to the hot water cylinder.[/QUOTE
Also if your boiler is installed in an unheated space such as a garage there is a possibility it could have a frost stat situated at the side of it wired to override any of the system controls.it will have a blank covered front , behind Being the
temp setting, if this was set too high say 5 / 7 degrees centigrade it could cause it to operate, especially now the temps have dropped.
Update:
I turned the boiler off for two hours. The meter reading was identical before and after. So (as anticipated) not a meter fault.
All three monitoring modes showed no gas usage during this time. So either a faulty zone valve as suggested by Plantagenet or could it be the towel rails or something else?
If they are hydronic towel rails, i.e. Piped, then they will be using boiler heat. If the boiler is off, nothing can be using gas. If something somewhere is calling for heat then the boiler will fire. Surely your boiler is also controlled by a timer, so even if something is calling for heat, the timer should cause the request to simply he ignored...unless it's an electrical fault and something is feeding past the timer.
Don't shoot me, I'm only the piano player. I DON'T work for or on behalf of EON.Next, but am willing to try and help if I can. Not on mains gas, mobile network or mains drainage. House heated almost entirely by baby dragons.
Because of the Tado system the heating side of the controller is set to always on. I really dont want to abandon Tado - I have invested a semi-fortune and it gives us complete control and lots of data on temperatures and calls for heat. I believe we have improved efficiency. Because of the complexity I have not used Tado for the HW. How is it that the towel rails are warm in the summer when none of the radiators are? Would it be linked to the HW?
I can tell that the thermostats are not calling for heat because the Tado app tells me when they are and this exactly correlates with hearing the TRV open and feeling the radiator warm up.
Any boiler based heating system needs a bypass loop. Possibly the towel radiators are acting as that loop.
There is something very wrong with a system that 'manages a heating system' in order to be 'more efficient', costs a fortune and runs your boiler at a minimum demand of 2-3kWh ever hour, 24/7.Try putting the heating side on 'timed' and switch off a 'window' between midnight and 7am. See what happens then
Sorry...it's clearly something your Tado system is not doing properly, or you do have some electrical issues somewhere. If you manually turn the boiler off....no gas consumption.
@MattB
I still suspect a control fault , irrespective of the timer calling for heat. A fault with a zone valve micro switch if stuck in the on position will pass a live current across the grey wire ( permanent live which is not timer controlled) to the orange wire feeding the boiler. Even if the zone valve is shut with no power to it's syncron motor. Any heat from the boiler could circulate through the bypass normal fitted after the pump but before the motorised valves back through the return pipe. This is fitted in addition to a radiator used as a bypass on the system.Your radiators etc would not heat up in this case. As the motorised valves would be closed allowing no flow through them .ie no power from timer/ stats.
Last edited by Plantagenet; 09-12-22 at 19:27.
Reason: Grammar
As with every diverse community, there is always a mixture of opinions, knowledge as well as understanding - that’s what makes it such a great place to be! To make sure everyone gets the most out of our Community and feels good doing it, we’ve created some values below on how to be an awesome, positive member. So, take a read and then go for it!
We love having you all here in the Community and really hope you find some great advice and help from our other amazing members. As a community team, our main role here is keeping things ticking over, everyone safe and getting involved in some great conversations! We know many of you will have specific queries about your accounts and we want to keep your personal details safe so please don't post them here.
• Saying thanks goes a long way
• The community is a public website, so be careful
• Be kind, respectful and supportive
• It's a family-friendly community
• If you’re in a specific section or discussion, try to stay on topic
• One post is normally enough
• Be cool, don’t spam
We want to ensure that the community is safe and fair for everyone…
We all work hard to ensure everyone feels respected and supported while using the community, and keep that positive energy flowing. If a member or group is disrupting your experience without a genuine reason, you can report this to the community team quickly and easily by clicking the 3 dots on the post. Don’t worry about a thing, we’ll take it from there. If you get a message from the team about your behaviour, please try to work with us, as all we want to do is make this a positive place for everyone. In order to this, we have to uphold these Community Values and the Community Team has the final say.
The full Community Values can be viewed here
If you agree, please click the 'I agree' checkbox and press the 'Complete Registration' button below. If you would like to cancel the registration, click here to return to the Community homepage.
Although the administrators and moderators of E.ON Next Community will attempt to keep all objectionable messages off this site, it is impossible for us to review all messages. All messages express the views of the author, and neither the owners of E.ON Next Community, nor vBulletin Solutions Inc. (developers of vBulletin) will be held responsible for the content of any message.
By agreeing to these rules, you warrant that you will not post any messages that are obscene, vulgar,sexually-oriented, hateful, threatening, or otherwise violative of any laws.
The owners of E.ON Next Community reserve the right to remove, edit, move or close any content item for any reason.